Message d'erreur
- Anonymous
- Auteur du sujet
- Membre platine
Moins
Plus d'informations
- Messages : 1608
- Remerciements reçus 0
il y a 12 ans 3 mois #5219
par Anonymous
Message d'erreur a été créé par Anonymous
Program Version,EnergyPlusDLL-OMP-32 7.2.0.006, 09/07/2013 18:36,IDD_Version 7.2.0.006
** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
************* Beginning Zone Sizing Calculations
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Warning ** Weather file location will be used rather than entered Location object.
** ~~~ ** ..Location object=ECOLE MATERNELLE
** ~~~ ** ..Weather File Location=PARIS_ ORLY - FRA IWEC Data WMO#=071490
** ~~~ ** ..due to location differences, Latitude difference=[0.24] degrees, Longitude difference=[5.00E-002] degrees.
** ~~~ ** ..Time Zone difference=[0.0] hour(s), Elevation difference=[47.69] percent, [31.00] meters.
** Warning ** WindowMaterial:Blind="30005", Slat Angles/Widths
** ~~~ ** Slat Width [7.00E-003] is less than Slat Separation [1.90E-002].
** ~~~ ** This will allow direct beam to be transmitted when Slat angle = 0.
** Severe ** FenestrationSurface:Detailed="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0_0_0_0_DOOR", invalid Building Surface Name="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0".
** ~~~ ** ... adiabatic surfaces cannot have windows or doors.
** ~~~ ** ... no solar transmission will result for these windows or doors. You must have interior windows or doors on Interzone surfaces for transmission to result.
** Severe ** FenestrationSurface:Detailed="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0_0_0_0_DOOR", invalid blank Outside Boundary Condition Object
** ~~~ ** ...when Base surface uses "Surface" as Outside Boundary Condition Object, subsurfaces must also specify specific surfaces in the adjacent zone.
** Warning ** GetSurfaceData: Construction 8 of interzone surface RDC:SALLEINFORMATIQUE_PARTITION_4_0_0 does not have the same materials in the reverse order as the construction 7 of adjacent surface RDC:CLASSE5_PARTITION_2_0_10000
** ~~~ ** ...but Nominal U values are similar, diff=[0.0000] ... simulation proceeds.
** ~~~ ** ...if the two zones are expected to have significantly different temperatures, the proper "reverse" construction should be created.
** ~~~ ** ...this problem for this pair will not be reported again.
** Fatal ** GetSurfaceData: Errors discovered, program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=2
..... Last severe error=FenestrationSurface:Detailed="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0_0_0_0_DOOR", invalid blank Outside Boundary Condition Object
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 4 Warning; 2 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 5 Warning; 2 Severe Errors; Elapsed Time=00hr 00min 2.32sec
Que signifie cette erreur ?
Merci
** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
************* Beginning Zone Sizing Calculations
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Warning ** Weather file location will be used rather than entered Location object.
** ~~~ ** ..Location object=ECOLE MATERNELLE
** ~~~ ** ..Weather File Location=PARIS_ ORLY - FRA IWEC Data WMO#=071490
** ~~~ ** ..due to location differences, Latitude difference=[0.24] degrees, Longitude difference=[5.00E-002] degrees.
** ~~~ ** ..Time Zone difference=[0.0] hour(s), Elevation difference=[47.69] percent, [31.00] meters.
** Warning ** WindowMaterial:Blind="30005", Slat Angles/Widths
** ~~~ ** Slat Width [7.00E-003] is less than Slat Separation [1.90E-002].
** ~~~ ** This will allow direct beam to be transmitted when Slat angle = 0.
** Severe ** FenestrationSurface:Detailed="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0_0_0_0_DOOR", invalid Building Surface Name="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0".
** ~~~ ** ... adiabatic surfaces cannot have windows or doors.
** ~~~ ** ... no solar transmission will result for these windows or doors. You must have interior windows or doors on Interzone surfaces for transmission to result.
** Severe ** FenestrationSurface:Detailed="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0_0_0_0_DOOR", invalid blank Outside Boundary Condition Object
** ~~~ ** ...when Base surface uses "Surface" as Outside Boundary Condition Object, subsurfaces must also specify specific surfaces in the adjacent zone.
** Warning ** GetSurfaceData: Construction 8 of interzone surface RDC:SALLEINFORMATIQUE_PARTITION_4_0_0 does not have the same materials in the reverse order as the construction 7 of adjacent surface RDC:CLASSE5_PARTITION_2_0_10000
** ~~~ ** ...but Nominal U values are similar, diff=[0.0000] ... simulation proceeds.
** ~~~ ** ...if the two zones are expected to have significantly different temperatures, the proper "reverse" construction should be created.
** ~~~ ** ...this problem for this pair will not be reported again.
** Fatal ** GetSurfaceData: Errors discovered, program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=2
..... Last severe error=FenestrationSurface:Detailed="RDC:SALLEINFORMATIQUE_PARTITION_5_0_0_0_0_0_DOOR", invalid blank Outside Boundary Condition Object
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 4 Warning; 2 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 5 Warning; 2 Severe Errors; Elapsed Time=00hr 00min 2.32sec
Que signifie cette erreur ?
Merci
Connexion pour participer à la conversation.
- Anonymous
- Auteur du sujet
- Membre platine
Moins
Plus d'informations
- Messages : 1608
- Remerciements reçus 0
il y a 12 ans 3 mois #5220
par Anonymous
Réponse de Anonymous sur le sujet Re: Message d'erreur
J'ai également eu cette erreur que je n'arrive pas à régler.
Restructuration Groupe scolaire Victor Hugo - Emile Zola - Groupe de zones invalide: Préau
Restructuration Groupe scolaire Victor Hugo - Emile Zola - Erreur de définition CVC
Restructuration Groupe scolaire Victor Hugo - Emile Zola - Groupe de zones invalide: Préau
Restructuration Groupe scolaire Victor Hugo - Emile Zola - Erreur de définition CVC
Connexion pour participer à la conversation.
- Anonymous
- Auteur du sujet
- Membre platine
Moins
Plus d'informations
- Messages : 1608
- Remerciements reçus 0
il y a 12 ans 3 mois #5224
par Anonymous
Réponse de Anonymous sur le sujet Re: Message d'erreur
Bonjour,
Votre premier message d'erreur parle d'une porte sur un mur adiabatique de RDC:SALLEINFORMATIQUE. Avez-vous une porte ou une sous-surface sur un mur adiabatique ?
Si oui, supprimez là pour éviter le problème.
Cordialement,
Votre premier message d'erreur parle d'une porte sur un mur adiabatique de RDC:SALLEINFORMATIQUE. Avez-vous une porte ou une sous-surface sur un mur adiabatique ?
Si oui, supprimez là pour éviter le problème.
Cordialement,