Message d'erreur

  • Anonymous
  • Auteur du sujet
  • Membre platine
Plus d'informations
il y a 12 ans 3 mois #5221 par Anonymous
Message d'erreur a été créé par Anonymous
Après modification de la STD j'obtient désormais le message d'erreur suivant qui est beaucoup plus long que les deux précédents (message précédent sur forum)..

Program Version,EnergyPlusDLL-OMP-32 7.2.0.006, 09/07/2013 18:50,IDD_Version 7.2.0.006
** Warning ** IP: Note -- Some missing fields have been filled with defaults. See the audit output file for details.
************* Beginning Zone Sizing Calculations
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Warning ** Weather file location will be used rather than entered Location object.
** ~~~ ** ..Location object=ECOLE MATERNELLE
** ~~~ ** ..Weather File Location=PARIS_ ORLY - FRA IWEC Data WMO#=071490
** ~~~ ** ..due to location differences, Latitude difference=[0.24] degrees, Longitude difference=[5.00E-002] degrees.
** ~~~ ** ..Time Zone difference=[0.0] hour(s), Elevation difference=[47.69] percent, [31.00] meters.
** Warning ** WindowMaterial:Blind="30005", Slat Angles/Widths
** ~~~ ** Slat Width [7.00E-003] is less than Slat Separation [1.90E-002].
** ~~~ ** This will allow direct beam to be transmitted when Slat angle = 0.
** Warning ** GetSurfaceData: Construction 8 of interzone surface RDC:SALLEINFORMATIQUE_PARTITION_4_0_0 does not have the same materials in the reverse order as the construction 7 of adjacent surface RDC:CLASSE5_PARTITION_2_0_10000
** ~~~ ** ...but Nominal U values are similar, diff=[0.0000] ... simulation proceeds.
** ~~~ ** ...if the two zones are expected to have significantly different temperatures, the proper "reverse" construction should be created.
** ~~~ ** ...this problem for this pair will not be reported again.
** Warning ** CheckUsedConstructions: There are 8 nominally unused constructions in input.
** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
** Warning ** Calculated design heating load for zone=RDC:SALLEINFORMATIQUE is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE4 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE2 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE1 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:PREAU is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:REPOS2 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:SALLED%ACTIVITE is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE5 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE9 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE8 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE7 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:CLASSE6 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=RDC:REPOS1 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
************* Beginning System Sizing Calculations
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 1" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 2" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 3" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 4" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 5" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 6" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 7" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 8" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE CLASSE 9" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF PRÉAU" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE DE JEUX & MOTRICITÉ" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF REPOS 1" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF REPOS 2" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE INFORMATIQUE" has no Controllers.
** Warning ** GetAirPathData: AirLoopHVAC="DF SALLE D'ACTIVITÉ" has no Controllers.
************* Beginning Plant Sizing Calculations
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:SALLEINFORMATIQUE RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE4 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE3 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE2 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE1 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:PREAU RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:SALLEDEJEUXMOTRICITE RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:REPOS2 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:SALLED%ACTIVITE RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE5 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE9 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE8 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE7 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:CLASSE6 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
** Warning ** The design coil load is zero for Coil:Heating:Water RDC:REPOS1 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** The autosize value for maximum water flow rate is zero
** ~~~ ** To change this, input a value for UA, change the heating design day, or lower
** ~~~ ** the system heating design supply air temperature
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
************* No node connection errors were found.
************* Beginning Simulation
** Warning ** Boiler:HotWater "CHAUDIÈRE SALLES"
** ~~~ ** ...Calculated Boiler Efficiency is greater than 1.1.
** ~~~ ** ...Boiler Efficiency calculations shown below.
** ~~~ ** ...Curve input x value (PLR) = 4.59680E-005
** ~~~ ** ...Curve input y value (Toutlet) = 60.00
** ~~~ ** ...Curve output (normalized eff) = 1.11193
** ~~~ ** ...Calculated Boiler efficiency = 1.11193 (Boiler efficiency = Nominal Thermal Efficiency * Normalized Boiler Efficiency Curve output)
** ~~~ ** ...Curve output reset to 1.1 and simulation continues.
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/01 00:00 - 00:15
** Warning ** Boiler:HotWater "EEEE"
** ~~~ ** ...Calculated Boiler Efficiency is greater than 1.1.
** ~~~ ** ...Boiler Efficiency calculations shown below.
** ~~~ ** ...Curve input x value (PLR) = 1.58300E-004
** ~~~ ** ...Curve input y value (Toutlet) = 60.00
** ~~~ ** ...Curve output (normalized eff) = 1.11193
** ~~~ ** ...Calculated Boiler efficiency = 1.11193 (Boiler efficiency = Nominal Thermal Efficiency * Normalized Boiler Efficiency Curve output)
** ~~~ ** ...Curve output reset to 1.1 and simulation continues.
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/01 00:00 - 00:15
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 00:00 - 00:05
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** ~~~ ** ...use Output:Diagnostics,DisplayExtraWarnings; to show more details on each max iteration exceeded.
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 00:15 - 00:30
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 00:40 - 00:45
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 00:45 - 00:52
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 01:00 - 01:15
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 01:00 - 01:08
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 01:15 - 01:22
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 01:35 - 01:40
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 01:40 - 01:45
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 01:55 - 02:00
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 02:00 - 02:08
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 02:15 - 02:22
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 02:35 - 02:40
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at ECOLE MATERNELLE, 01/01 02:40 - 02:45
** ~~~ ** The solution for zone HVAC equipment did not appear to converge
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:ATSEM RADIATEUR EAU
** ~~~ ** ... Load met = 68.11730 W.
** ~~~ ** ... Load requested = 47.28275 W.
** ~~~ ** ... Error = 20.83455848 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =1.128567989E-009 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/01 07:12 - 07:14
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:MAITRES RADIATEUR EAU
** ~~~ ** ... Load met = 37.03643 W.
** ~~~ ** ... Load requested = 31.04264 W.
** ~~~ ** ... Error = 5.99378789 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =1.061970836E-009 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/01 07:14 - 07:15
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:CLASSE3 RADIATEUR EAU
** ~~~ ** ... Load met = 10.85947 W.
** ~~~ ** ... Load requested = 8.80888 W.
** ~~~ ** ... Error = 2.05058429 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =2.055737800E-009 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/01 09:23 - 09:30
** Warning ** Boiler:HotWater "CHAUDIÈRE/1"
** ~~~ ** ...Calculated Boiler Efficiency is greater than 1.1.
** ~~~ ** ...Boiler Efficiency calculations shown below.
** ~~~ ** ...Curve input x value (PLR) = 3.33812E-006
** ~~~ ** ...Curve input y value (Toutlet) = 60.00
** ~~~ ** ...Curve output (normalized eff) = 1.11193
** ~~~ ** ...Calculated Boiler efficiency = 1.11193 (Boiler efficiency = Nominal Thermal Efficiency * Normalized Boiler Efficiency Curve output)
** ~~~ ** ...Curve output reset to 1.1 and simulation continues.
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/04 20:00 - 20:15
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:SANITAIRES RADIATEUR EAU
** ~~~ ** ... Load met = 63.52626 W.
** ~~~ ** ... Load requested = 25.73801 W.
** ~~~ ** ... Error = 37.78824600 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =1.326226863E-009 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/07 11:00 - 11:15
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:SALLEDEJEUXMOTRICITE RADIATEUR EAU
** ~~~ ** ... Load met = 140.33524 W.
** ~~~ ** ... Load requested = 114.21522 W.
** ~~~ ** ... Error = 22.86911733 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =5.234661163E-009 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/07 17:34 - 17:36
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:DIRECTION RADIATEUR EAU
** ~~~ ** ... Load met = 0.00000 W.
** ~~~ ** ... Load requested = 17.55979 W.
** ~~~ ** ... Error = 17.55979531 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =0.000000000 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/08 07:11 - 07:12
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:CIRCULATIONEST RADIATEUR EAU
** ~~~ ** ... Load met = 5.00494 W.
** ~~~ ** ... Load requested = 3.37617 W.
** ~~~ ** ... Error = 1.62876920 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =3.329111496E-009 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/10 15:15 - 15:30
** Warning ** GetSpecificHeatGlycol: Temperature is out of range (too low) for fluid [WATER] specific heat **
** ~~~ ** ..Called From:PlantLoopSolver::EvaluateLoopSetPointLoad,Temperature=-70501.62
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/14 07:42 - 07:43
** Warning ** GetSpecificHeatGlycol: Temperature is out of range (too low) for fluid [WATER] density **
** ~~~ ** ..Called From:PlantPumps:CalcPumps:,Temperature=-70501.62
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/14 07:42 - 07:43
** Warning ** GetSpecificHeatGlycol: Temperature is out of range (too high) for fluid [WATER] specific heat **
** ~~~ ** ..Called From:PlantLoopSolver::EvaluateLoopSetPointLoad,Temperature=156.86
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/14 07:42 - 07:43
** Warning ** ControlCompOutput: Maximum iterations exceeded for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:CIROUEST RADIATEUR EAU
** ~~~ ** ... Load met = 314.93068 W.
** ~~~ ** ... Load requested = 297.75339 W.
** ~~~ ** ... Error = 5.76896566 %.
** ~~~ ** ... Tolerance = 1.00000000 %.
** ~~~ ** ... Error = (Load met - Load requested) / MAXIMUM(Load requested, 100)
** ~~~ ** ... Actuated Node Mass Flow Rate =8.182019187E-003 kg/s
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/15 10:23 - 10:30
** Warning ** GetSpecificHeatGlycol: Temperature is out of range (too high) for fluid [WATER] density **
** ~~~ ** ..Called From:PlantPumps:CalcPumps:,Temperature=227886.70
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/17 07:43 - 07:44
** Severe ** Plant temperatures are getting far too hot, check controls and relative loads and capacities
** ~~~ ** Environment=ECOLE MATERNELLE, at Simulation time=01/17 07:43 - 07:44
** ~~~ ** PlantLoop Name (SupplySide)= SOUS-STATION 2
** ~~~ ** PlantLoop Setpoint Temperature=80.0 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) does not have a Setpoint.
** ~~~ ** PlantLoop Inlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) has a Setpoint.
** ~~~ ** PlantLoop Outlet Node (DemandSide) does not have a Setpoint.
** ~~~ ** PlantLoop Outlet Node (SupplySide) "SOUS-STATION 2 SUPPLY SIDE OUTLET" has temperature=227886.7 {C}
** ~~~ ** PlantLoop Inlet Node (SupplySide) "SOUS-STATION 2 SUPPLY SIDE INLET" has temperature=227886.7 {C}
** ~~~ ** PlantLoop Minimum Temperature=20.0 {C}
** ~~~ ** PlantLoop Maximum Temperature=60.0 {C}
** ~~~ ** PlantLoop Flow Request (SupplySide)=3.4E-002 {kg/s}
** ~~~ ** PlantLoop Flow Request (DemandSide)=2.1E-009 {kg/s}
** ~~~ ** PlantLoop Node (SupplySide) "SOUS-STATION 2 SUPPLY SIDE OUTLET" has mass flow rate =2.1E-009 {kg/s}
** ~~~ ** PlantLoop PumpHeat (SupplySide)=442.2 {W}
** ~~~ ** PlantLoop PumpHeat (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Cooling Demand=2.0 {W}
** ~~~ ** PlantLoop Heating Demand=0.0 {W}
** ~~~ ** PlantLoop Demand not Dispatched=0.0 {W}
** ~~~ ** PlantLoop Unmet Demand=-2.0 {W}
** ~~~ ** PlantLoop Capacity=300000.0 {W}
** ~~~ ** PlantLoop Capacity (SupplySide)=300000.0 {W}
** ~~~ ** PlantLoop Capacity (DemandSide)=0.0 {W}
** ~~~ ** PlantLoop Operation Scheme=SOUS-STATION 2 FONCTIONNEMENT
** ~~~ ** PlantLoop Operation Dispatched Load = 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (SupplySide)= 0.0 {W}
** ~~~ ** PlantLoop Operation Dispatched Load (DemandSide)= 0.0 {W}
** ~~~ ** Branches on the Loop.
** ~~~ ** Demand Branches:
** ~~~ ** SOUS-STATION 2 DEMAND SIDE INLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:SOUS-STATION 2 DEMAND SIDE INLET BRANCH PIPE
** ~~~ ** RDC:CLASSE9 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE9 RADIATEUR EAU
** ~~~ ** RDC:CLASSE8 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE8 RADIATEUR EAU
** ~~~ ** RDC:CLASSE7 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE7 RADIATEUR EAU
** ~~~ ** RDC:CLASSE6 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE6 RADIATEUR EAU
** ~~~ ** RDC:SALLED%ACTIVITE RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:SALLED%ACTIVITE RADIATEUR EAU
** ~~~ ** RDC:SALLED%ACTIVITE RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:SALLED%ACTIVITE RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE6 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE6 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE7 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE7 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE8 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE8 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE9 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE9 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE5 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE5 RADIATEUR EAU
** ~~~ ** RDC:CLASSE4 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE4 RADIATEUR EAU
** ~~~ ** RDC:CLASSE3 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE3 RADIATEUR EAU
** ~~~ ** RDC:CLASSE2 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE2 RADIATEUR EAU
** ~~~ ** RDC:CLASSE1 RADIATEUR EAU HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** ZONEHVAC:BASEBOARD:RADIANTCONVECTIVE:WATER:RDC:CLASSE1 RADIATEUR EAU
** ~~~ ** RDC:CLASSE1 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE1 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE2 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE2 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE3 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE3 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE4 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE4 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** RDC:CLASSE5 RÉCHAUFFAGE VAV BATTERIE CHAUDE HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** COIL:HEATING:WATER:RDC:CLASSE5 RÉCHAUFFAGE VAV BATTERIE CHAUDE
** ~~~ ** SOUS-STATION 2 DEMAND SIDE OUTLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:SOUS-STATION 2 DEMAND SIDE OUTLET BRANCH PIPE
** ~~~ ** Supply Branches:
** ~~~ ** SOUS-STATION 2 SUPPLY SIDE INLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PUMP:CONSTANTSPEED:SOUS-STATION 2 SUPPLY POMPE
** ~~~ ** SOUS-STATION 2 SUPPLY SIDE BYPASS BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:SOUS-STATION 2 SUPPLY SIDE BYPASS PIPE
** ~~~ ** CHAUDIÈRE/1 HW PLANT LOOP BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** BOILER:HOTWATER:CHAUDIÈRE/1
** ~~~ ** SOUS-STATION 2 SUPPLY SIDE OUTLET BRANCH
** ~~~ ** Components on Branch:
** ~~~ ** PIPE:ADIABATIC:SOUS-STATION 2 SUPPLY SIDE OUTLET BRANCH PIPE
** ~~~ ** *************************
** ~~~ ** Possible things to look for to correct this problem are:
** ~~~ ** Capacity, Operation Scheme, Mass flow problems, Pump Heat building up over time.
** ~~~ ** Try a shorter runperiod to stop before it fatals and look at
** ~~~ ** lots of node time series data to see what is going wrong.
** ~~~ ** If this is happening during Warmup, you can use Output:Diagnostics,ReportDuringWarmup;
** ~~~ ** This is detected at the loop level, but the typical problems are in the components.
** Fatal ** CheckForRunawayPlantTemps: Simulation terminated because of run away plant temperatures, too hot
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=Plant temperatures are getting far too hot, check controls and relative loads and capacities
** Warning ** There is no BYPASS component in the demand-side of PlantLoop =SOUS-STATION
** ~~~ ** You may be able to fix the fatal error above by adding a demand-side BYPASS PIPE.
** Warning ** There is no BYPASS component in the demand-side of PlantLoop =SOUS-STATION 2
** ~~~ ** You may be able to fix the fatal error above by adding a demand-side BYPASS PIPE.
** Warning ** There is no BYPASS component in the demand-side of PlantLoop =HW LOOP SANIATIRES
** ~~~ ** You may be able to fix the fatal error above by adding a demand-side BYPASS PIPE.
*************
************* ===== Recurring Error Summary =====
************* The following recurring error messages occurred.
*************
************* ** Warning ** Boiler:HotWater "CHAUDIÈRE SALLES": Calculated Boiler Efficiency is greater than 1.1 warning continues...
************* ** ~~~ ** This error occurred 152855 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=1.111966 Min=1.111933
*************
************* ** Warning ** Boiler:HotWater "EEEE": Calculated Boiler Efficiency is greater than 1.1 warning continues...
************* ** ~~~ ** This error occurred 236627 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=1.111983 Min=1.111933
*************
************* ** Warning ** SimHVAC: Exceeding Maximum iterations for all HVAC loops, during ECOLE MATERNELLE continues
************* ** ~~~ ** This error occurred 2108 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:ATSEM RADIATEUR EAU
************* ** ~~~ ** This error occurred 44 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=31.40472 % Min=3.650293 %
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:MAITRES RADIATEUR EAU
************* ** ~~~ ** This error occurred 75 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=11.213068 % Min=2.452931 %
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:CLASSE3 RADIATEUR EAU
************* ** ~~~ ** This error occurred 29 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=93.713765 % Min=2.050584 %
*************
************* ** Warning ** Boiler:HotWater "CHAUDIÈRE/1": Calculated Boiler Efficiency is greater than 1.1 warning continues...
************* ** ~~~ ** This error occurred 88823 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=1.111933 Min=1.111933
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:SANITAIRES RADIATEUR EAU
************* ** ~~~ ** This error occurred 23 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=37.788255 % Min=37.788246 %
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:SALLEDEJEUXMOTRICITE RADIATEUR EAU
************* ** ~~~ ** This error occurred 2 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=22.869117 % Min=22.869117 %
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:DIRECTION RADIATEUR EAU
************* ** ~~~ ** This error occurred 23 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=17.559795 % Min=17.559795 %
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:CIRCULATIONEST RADIATEUR EAU
************* ** ~~~ ** This error occurred 8 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=1.628769 % Min=1.628688 %
*************
************* ** Warning ** GetSpecificHeatGlycol: Temperature out of range (too low) for fluid [WATER] specific heat **
************* ** ~~~ ** This error occurred 256 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=-70501.622218 {C} Min=-70501.773309 {C}
*************
************* ** Warning ** GetSpecificHeatGlycol: Temperature out of range (too low) for fluid [WATER] density **
************* ** ~~~ ** This error occurred 64 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=-70501.622218 {C} Min=-70501.773309 {C}
*************
************* ** Warning ** GetSpecificHeatGlycol: Temperature out of range (too high) for fluid [WATER] specific heat **
************* ** ~~~ ** This error occurred 298 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=227886.698111 {C} Min=156.863897 {C}
*************
************* ** Warning ** ControlCompOutput: Maximum iterations error for ZoneHVAC:Baseboard:RadiantConvective:Water = RDC:CIROUEST RADIATEUR EAU
************* ** ~~~ ** This error occurred 23 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=5.768966 % Min=5.768749 %
*************
************* ** Warning ** GetSpecificHeatGlycol: Temperature out of range (too high) for fluid [WATER] density **
************* ** ~~~ ** This error occurred 4 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=227886.698111 {C} Min=227886.698111 {C}
*************
************* ** Warning ** Plant loop exceeding upper temperature limit, PlantLoop="SOUS-STATION 2"
************* ** ~~~ ** This error occurred 1 total times;
************* ** ~~~ ** during Warmup 0 times;
************* ** ~~~ ** during Sizing 0 times.
************* ** ~~~ ** Max=227886.698111
*************
*************
************* ===== Final Error Summary =====
************* The following error categories occurred. Consider correcting or noting.
************* Nominally Unused Constructions
************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause
************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm
************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 33 Warning; 0 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 481332 Warning; 1 Severe Errors; Elapsed Time=00hr 10min 32.51sec

Connexion pour participer à la conversation.

  • Anonymous
  • Auteur du sujet
  • Membre platine
Plus d'informations
il y a 12 ans 3 mois #5225 par Anonymous
Réponse de Anonymous sur le sujet Re: Message d'erreur
Bonjour,

Ce message concerne une boucle d'eau chaude nommée Sous Station 2. Sa température diverge et atteint des valeurs trop élevées.

D'après les alertes (Warnings) d'EnergyPlus vous avez un problème de paramétrage de votre CVC.
Les batteries chaudes de nombreuses zones sont dimensionnées à zéro. Des chaudières auraient un rendement qui dépasse 110% à cause de la courbe de performance qui leur a été associé.
Bref, il y a certainement un manque de demande et peut être une permanence de la production de chaleur qui engendre une élévation de température anormale.

Valider d'abord votre dimensionnement d'émetteur (cliquez sur les Rapports Annuels de Dimensionnement avant de lancer votre simulation) et reprenez le paramétrage de vos chaudières
pour qu'elles restent dans une plage de fonctionnement réaliste.

Cordialement,