Compile en été affiche des erreurs en hiver

  • Anonymous
  • Auteur du sujet
  • Membre platine
Plus d'informations
il y a 11 ans 6 mois #5385 par Anonymous
Compile en été affiche des erreurs en hiver a été créé par Anonymous
Bonjour,

J'étudie l'isolation d'un bâtiment par double façade. J'arrive à lancer la simulation pour une semaine d'été, mais je reçois quelque 8 warning et 3642 severes pour l'hiver ou la simu annuelle.

Je reçois :
Program Version,EnergyPlusDLL-32 8.1.0.008, 15/04/2014 11:56,IDD_Version 8.1.0.008
** Warning ** Timestep: Requested number (2) is less than the suggested minimum of 4.
** ~~~ ** Please see entry for Timestep in Input/Output Reference for discussion of considerations.
************* Beginning Zone Sizing Calculations
** Warning ** Weather file location will be used rather than entered (IDF) Location object.
** ~~~ ** ..Location object=SANS TITRE
** ~~~ ** ..Weather File Location=MONTPELLIER - FRA IWEC Data WMO#=076430
** ~~~ ** ..due to location differences, Latitude difference=[5.00E-002] degrees, Longitude difference=[2.60] degrees.
** ~~~ ** ..Time Zone difference=[0.0] hour(s), Elevation difference=[96.08] percent, [147.00] meters.
** Warning ** GetSurfaceData: Construction PROJET DE CLOISON of interzone surface RDC:ZONE1_PARTITION_7_0_0 does not have the same materials in the reverse order as the construction PROJET DE CLOISON_REV of adjacent surface FDPPASSAGE:ZONE1_PARTITION_50_0_10003
** ~~~ ** ...but Nominal U values are similar, diff=[0.0000] ... simulation proceeds.
** ~~~ ** ...if the two zones are expected to have significantly different temperatures, the proper "reverse" construction should be created.
** ~~~ ** ...this problem for this pair will not be reported again.
** Warning ** GetSurfaceData: CAUTION -- Interzone surfaces are occuring in the same zone(s).
** ~~~ ** ...use Output:Diagnostics,DisplayExtraWarnings; to show more details on individual occurrences.
** Warning ** GetSurfaceData: Entered Zone Floor Areas differ from calculated Zone Floor Area(s).
** ~~~ ** ...use Output:Diagnostics,DisplayExtraWarnings; to show more details on individual zones.
** Warning ** CalcSurfaceCentroid: 6 Surfaces have the Z coordinate < 0.
** ~~~ ** ...in any calculations, Wind Speed will be 0.0 for these surfaces.
** ~~~ ** ...in any calculations, Outside temperatures will be the outside temperature + 9.750E-003 for these surfaces.
** ~~~ ** ...that is, these surfaces will have conditions as though at ground level.
************* Note that the following warning(s) may/will occur if you have not enclosed your zone completely.
** Warning ** Entered Zone Volumes differ from calculated zone volume(s).
** ~~~ ** ...use Output:Diagnostics,DisplayExtraWarnings; to show more details on individual zones.
** Warning ** CheckUsedConstructions: There are 8 nominally unused constructions in input.
** ~~~ ** For explicit details on each unused construction, use Output:Diagnostics,DisplayExtraWarnings;
** Severe ** Problem in interior solar distribution calculation (CHKBKS)
** ~~~ ** Solar Distribution = FullInteriorExterior will not work in Zone=RDC:ZONE1
** ~~~ ** because vertex 3 of back surface=RDC:ZONE1_WALL_4_0_0 is in front of receiving surface=RDC:ZONE1_WALL_3_0_0
** ~~~ ** (Dot Product indicator=21.8899)
** ~~~ ** Check surface geometry; if OK, use Solar Distribution = FullExterior instead.

Ce cernier severe est affiché pour chaque vertex de chaque mur de chaque zone... donc beaucoup de fois.
Puis le message finit par :

** Severe ** Problem in interior solar distribution calculation (CHKBKS)
** ~~~ ** Solar Distribution = FullInteriorExterior will not work in Zone=FDPENTREE:ZONE1
** ~~~ ** because vertex 2 of back surface=FDPENTREE:ZONE1_ROOF_10_0_0 is in front of receiving surface=FDPENTREE:ZONE1_WALL_3_0_1
** ~~~ ** (Dot Product indicator=3.7070)
** ~~~ ** Check surface geometry; if OK, use Solar Distribution = FullExterior instead.
** Severe ** Temperature (high) out of bounds (5626.79] for zone="FDPRUE:ZONE1", for surface="FDPRUE:ZONE1_PARTITION_55_0_10175"
** ~~~ ** During Warmup & Sizing, Environment=SUMMER DESIGN DAY IN SANS TITRE, at Simulation time=07/15 07:30 - 07:36
** ~~~ ** Zone="FDPRUE:ZONE1", Diagnostic Details:
** ~~~ ** ...Internal Heat Gain [31.770] W/m2
** ~~~ ** ...Infiltration/Ventilation [4.491E-002] m3/s
** ~~~ ** ...Mixing/Cross Mixing [0.000] m3/s
** ~~~ ** ...Zone is part of HVAC controlled system.
** Fatal ** CalcHeatBalanceInsideSurf: Program terminates due to preceding conditions.
...Summary of Errors that led to program termination:
..... Reference severe error count=3643
..... Last severe error=Temperature (high) out of bounds (5626.79] for zone="FDPRUE:ZONE1", for surface="FDPRUE:ZONE1_PARTITION_55_0_10175"
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*************
************* ===== Recurring Error Summary =====
************* The following recurring error messages occurred.
*************
************* ** Severe ** Temperature (high) out of bounds for zone=FDPRUE:ZONE1 for surface=FDPRUE:ZONE1_PARTITION_55_0_10175
************* ** ~~~ ** This error occurred 1 total times;
************* ** ~~~ ** during Warmup 1 times;
************* ** ~~~ ** during Sizing 1 times.
************* ** ~~~ ** Max=5626.79444 C Min=5626.79444 C
*************
*************
************* ===== Final Error Summary =====
************* The following error categories occurred. Consider correcting or noting.
************* Interzone surfaces - different zones
************* Temperature (high) out of bounds
************* ..A temperature out of bounds problem can be caused by several things. The user should check:
************* ..1) the weather environment (including the horizontal IR from sky)
************* ..2) the level of interal gains with respect to the zone
************* ..3) the thermal properties of their materials. And other things.
************* ..A common cause is a building with no or little thermal mass - all materials with Material:NoMassdefinitions.
************* Nominally Unused Constructions
************* ..The nominally unused constructions warning is provided to alert you to potential conditions that can cause
************* ..extra time during simulation. Each construction is calculated by the algorithm indicated in the HeatBalanceAlgorithm
************* ..object. You may remove the constructions indicated (when you use the DisplayExtraWarnings option).
*************
************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors.
************* EnergyPlus Sizing Error Summary. During Sizing: 7 Warning; 3642 Severe Errors.
************* EnergyPlus Terminated--Fatal Error Detected. 8 Warning; 3643 Severe Errors; Elapsed Time=00hr 09min 29.28sec

Pour être franc je viens de me mettre sur DB et je ne comprends pas vraiment tout ce que cela signifie. Je suppose qu'il s'agit d'une erreur que se répercute partout. La convergence du modèle peut-être ? Avez-vous une idée ?

Merci à vous

Coco

Connexion pour participer à la conversation.

  • Anonymous
  • Auteur du sujet
  • Membre platine
Plus d'informations
il y a 11 ans 6 mois #5386 par Anonymous
Réponse de Anonymous sur le sujet Re: Compile en été affiche des erreurs en hiver
Bonjour,

Les premiers messages indiquent un problème de calcul de la quantité d'ensoleillement atteignant des surfaces. Ces erreurs ne stoppent pas le calcul mais signifient
que le flux solaire est mal pris en compte. Dans votre cas, une surface fait de l'ombre à une autre mais n'est pas prise en compte.
Ceci est du au fait que vous avez choisi la Distribution solaire intérieure et extérieure complète. E+ est limité dans son calcul à des zones convexes, si ce n'est pas le cas
il émet une erreur. Vos zones sont certainement non convexes (toutes les parois doivent se voir l'une l'autre sans passer au travers d'une autre).

Enfin, la dernière erreur qui arrête le programme est due à une divergence des calculs de température pour la cloison FDPRUE:ZONE1_PARTITION_55_0_10175 de la zone FDPRUE ZONE 1,
la température atteint plus de 5000 °C donc il y a un problème de paramétrage. Ce peut être du :
  • La surface trop petite de la cloison étant donné le flux de chaleur qui l'atteint
  • Elle est adiabatique et la chaleur n'arrive pas à être évacuée
  • Les matériaux très inertiques provoquent cette divergence

Pour retrouver cette cloison dans votre modèle, cliquez sur les cloisons de la zone en regardant dans l'onglet Sortie > Simulation, le code E+ est affiché ici.

Cordialement,

Connexion pour participer à la conversation.

  • Anonymous
  • Auteur du sujet
  • Membre platine
Plus d'informations
il y a 11 ans 6 mois #5390 par Anonymous
Réponse de Anonymous sur le sujet Re: Compile en été affiche des erreurs en hiver
Bonjour,

Merci d'avoir répondu. Cela marche maintenant!

Connexion pour participer à la conversation.